Converting Electric Dryer from 3 wire to 4 wire

Automatic Washer - The world's coolest Washing Machines, Dryers and Dishwashers

Help Support :

kenmore70

Well-known member
Platinum Member
Joined
Feb 24, 2013
Messages
48
Location
New York
I want to convert a Kenmore Dryer power cord from 3 wire to 4 wire since I have a four prong outlet. Currently, on the machine the neutral grounding wire (green) is connected to the external grounding screw, and the other end is attached to the center terminal block screw. When attaching the new green wire from the power cord, I will now attach that to the external grounding screw. What should be done with the end of the current green external connector (the green wire in the picture to the right with the round spade)? Right now the other end is attached to the spade with the neutral wire at the center terminal, I could just cut it off or does that go back on the external ground screw also with the ground wire from the power cord?

kenmore70++9-7-2013-13-16-0.jpg
 
arbilab is Correct

Unfortunately it's a big no-no to connect the neutral & ground together on the load side: 

<span style="font-family: tahoma,arial,helvetica,sans-serif;">"</span><span style="font-family: Times New Roman;"><span style="font-family: tahoma,arial,helvetica,sans-serif;">The National Electrical Code requires a neutral-to-ground connection to be made at service equipment only and there shall not be any neutral-to-ground connection on the load side of service equipment [250-23(a), <span class="bodyitalic">250-24(a)(5)</span>], except as permitted in Section 250-61 [<span class="bodyitalic">250-142</span>]." </span> </span>

<span style="font-family: Times New Roman;"> </span>

<span style="font-family: Times New Roman;">You need to use all four conductors of your receptacle/power cord to comply with the code.</span>
 
Converting from a three wire power cord to a 4 wire cord

Tom I read your first post too fast, and as two other folks noticed, the existing green wire does NOT go back where it was, I though that you meant that you were going to put it on the screw where the white wires go which is what I said in my response. And while you could just cut off this green jumper-ground wire the preferred place to put it would be back on the white neutral terminal in case someone wanted to use the dryer with a 3 wire hook-up in the future.
 
Converting to new 4 wire outlets

Clever idea Martin, I guess it was only a matter of time till someone came out with these. They sort of glossed over what to do with that green wire that needs to be connected to a good ground in the video when converting a older 3 wire outlet to accept a 4 prong plug, LOL.

 

I wounder how soon that manufactures will start warning consumers not to use an ADAPTER, like they have done with the 120 three pronged adapters for the last 30 years.

 

The bad thing about these adapters is you have two HIGH CURRENT connections stacked on top of each other, which will more than double the risk of heat build-up and failure or even possible fire at the outlet area.
 