The Electricity’s Out Again—Certain Outlets, Certain Rooms!

Automatic Washer - The world's coolest Washing Machines, Dryers and Dishwashers

Help Support :

daveamkrayoguy

Well-known member
Platinum Member
Joined
Dec 8, 2010
Messages
5,214
Location
Oak Park, MI
Yes, what happened months ago, in our master bathroom, and my bedroom... And the light fixtures, wall for the former, ceiling for the latter, don’t go on, either...

Only instead of running another extension cord for my stereo, I just decided to contend with “what’s just another power failure” being glad everything else works in the house that’s electrical, like the dishwasher and especially the fridge...

Must not be anyone else with this problem, as the electric company seems slow in getting this sort of thing repaired...

— Dave
 
Electricity

Sounds like Squirrels have chewed through one of the lines from the pole to the house. I had a similar issue a few years ago where power in half he house went out. The power company (SCG&E) came out and replaced the line at no charge! Good luck!
 
power

Dave,

Maybe I am misconstruing your problem. However, if you have select circuits in your house that are not functioning, that has nothing to do with the "electric company."

Your problem is within you home's wiring. Your electric company's responsibility is to deliver power to your meter, after exiting the meter becomes your responsibility. From the meter it goes to your distribution (breaker or fuse) panel box. Then it goes to each individual circuit within the house.

Always check your breakers/fuses first. If you have breakers and can't see which one is tripped, go down and cycle each breaker by hand, eventually you will reset the tripped one.

Other causes, but less easy to find:

A breaker can go bad. It is not common but can happen. The screw holding down the hot line on a given breaker could be loose as well.

A loose connection somewhere within the circuit can cause an outage. My sister/brother-in-law moved into an older house where the previous owner had changed out an outletm but failed to tighten the contact screws that held the wiring down. Whenever anyone walked through the dinning room, the vibrations made the dinning room light and the dishwasher in the kitchen go on and off. They were both on the same circuit downstream of the outlet with the loose contact screws. (A doubly bad situation as code require a dishwasher to be on a separate circuit and the owner had just added it to a regular household lighting/outlet circuit.)

If you are not familiar with working with electrical components then don't go messing around in your outlets or panel box. Electricity can be unforgiving, and you could get shocked badly or even encounter a lethal situation resulting in electrocution.

I would recommend you hire someone qualified to check your individual circuits and repair the offending one. Please do it soon as a loose electrical connection can possibly arc and cause a fire.
 
addendum

I just read Brainard's post. He did mention one scenario that could cause select circuits to go out, and yet occur before your meter, and be the power companies responsibility.

You have two two 120 volt "legs" that come in from the power company. If one is broken (open) everything on that leg will be out in your house. If this is the case NO 240 volt appliance in your home will work, as all require both 120v legs to combine to give yo 240 volts.

So if that scenario is true you will have no hot water, your dryer will not heat, your burners and oven will not function, etc.

If your 240 volt appliances all work, then the problem is not outside, but as stated in my previous posting, within your home's wiring.
 
If you have a GFI circuit switch on one of your outlets, usually they are in a bathroom, see if the button needs to be reset. If so, push it in and then try the the switches that weren’t working, if the lights go on, then you’ve found your problem.

The outlet in our backyard, light over the kitchen sink, DW, and front porch light are all connected to a GFI circuit. If any of these lights/outlets fail to function then I know the GFI has tripped and needs to be reset. I hope that this solves your problem.

Eddie
 
GFCI

As Eddie said it COULD be GFCI, but you indicated it was your bedroom. Usually a GFCI has other bathrooms, outdoor receptacles and/or kitchen receptacles downstream. Circuits that require GFCI protection.

However, with the way people wire things nowdays, it could be your bedroom lights are downstream of the GFCI in your bath. Eddie is right, try it. Always start with the simplest scenarios then work up!
 
As was said, the power company is only concerned about the the wires up to your house or into the meter socket.  Any thing after that you need to fix yourself or hire someone to.

 

Though it could be a GFI, because it's in a living room where GFI's usually are not used, it sounds like something other. 

 

 

I had a situation similar to what your describing and it was the result of one simple wire that come loose off of an outlet. That one wire caused a number of other outlets and fixtures to not work.  The trick was to find which one was loose. 

 

Doing a complete map of all the electrical devices in your home helps to pinpoint these type problems.

bradfordwhite-2019121111225608272_1.png
 
Dave,

before calling in an electrician, check the most obvious and simple problem first. A with a car that won't crank over, it's usually the battery.
Wire connections on the wal recepticles and or switches can loosen with time anbd temperature fluctuations. Because house wiring is multiplexed with more than one room on a circuit, one loose connection can cause outlets other than the one to be dead. I've had it happen even in summer.
 
>> Always check your breakers/fuses first. If you have breakers and can't see which one is tripped, go
>> down and cycle each breaker by hand, eventually you will reset the tripped one.

And of course, if you find a breaker that has tripped without indicating, that is a rather significant failure of the breaker, and it should be replaced. (And toggled to off in the meantime while waiting for the new breaker to be installed, as the safety and functionality of that breaker is now suspect.)

>> You have two two 120 volt "legs" that come in from the power company. If one is broken (open) everything
>> on that leg will be out in your house. If this is the case NO 240 volt appliance in your home will work, as all
>> require both 120v legs to combine to give yo 240 volts. So if that scenario is true you will have no hot
>> water, your dryer will not heat, your burners and oven will not function, etc.

That's only conditionally true, depending on the appliance. Many 240V appliances in the USA use the two 120V legs independently, so you may only see partial impacts (or no impact at all) from the loss of one leg, depending on how you are using the appliance. For example, my combination wall oven is a 240V appliance - but the microwave component is wired from just one of the 120V legs, as is the control panel, interior lights, etc, from the oven portion. So I could loose power from one phase, and the oven would "seem" fine or the microwave work as normal. Likewise, many dryers use 240V for the heating element, but 120V for the motor, timer, etc. So it may seem like the dryer is operating just fine (just not noticing that it isn't heating)... or it may even be that you selected an air-fluff cycle, and it genuinely *is* operating just fine with half of its power circuit missing.
 
>> As Eddie said it COULD be GFCI, but you indicated it was your bedroom. Usually a GFCI has other bathrooms,
>> outdoor receptacles and/or kitchen receptacles downstream. Circuits that require GFCI protection.

That's actually not too unusual for a bedroom anymore, at least on newer houses.

The National Electric Code has required arc-fault protection for bedroom receptacles in new construction since 1999, before requiring that for any other room of the house. And a few years later they made it so that bedroom lighting also had to be arc-fault protected. If I remember correctly, the reasoning was that they wanted arc-fault protection everywhere, but had to start somewhere, and bedrooms were the arbitrary starting point they picked.

Now in terms of arc-fault vs ground-fault protection, the codes do still require ground-fault protection in bathrooms, kitchens, laundry areas, etc, even though whole-house arc-fault protection is now mandatory. The result is that the "dual-function" CAFCI+GFCI breakers in some cases are now cheaper than arc-fault breakers due to supply and demand, and for electricians doing repairs or new installs, having a big box of dual-function breakers that work for everything is a lot simpler than separately stocking arc-fault and arc+ground fault breakers and selectively using them.

So it wouldn't be too surprising to find a bedroom on a ground-fault protected circuit nowadays.
 
tripping/240v appliances

Dave,

Some brands of breakers are difficult to determine if tripped. Some have indicators, some do not, and some have barely perceptible or non-perceptible movement of the lever. I have a Westinghouse (pre-Bryant ) breaker panel box in my current home where I have to cycle the breakers anytime I have a trip because that cannot be determined visually. That does not necessarily mean the breakers are bad.

I stand by my statement that 240 volt appliances will not function on one 120v leg. If you go back and read my statement you see that it says, "your dryer will not heat." Yes, the motor may rotate the drum, dependent on which leg is still energized. Whether the drum rotates or not, a dryer that is not heating is not functioning.

If someone thinks a dryer is not heating because they put it on "fluff," they would set the control to a heated cycle and see that indeed the dryer is not working.

Likewise, it was stated that a "burner" and "oven" would not work on one 120 volt let.....and they will not. Yes, the light in the oven could come on (once again dependent of which leg is supplying current), but that does not mean the oven is working. Heat indicates a working oven, and that will not happen with one 120 leg being non-functional.

Yes, if you re-read my statement, it said the bedroom COULD be on a GFCI circuit. However, it is not the norm. Most people are not living in a "new" home and not every "new" home has the bedroom on a GFCI protected circuit.
 
Well, yes, I'd gone to the breaker box, and not one switch was tripped, and although the panels are well-marked, I couldn't bear with resetting clocks, just randomly flipping switches, as that idea did nothing to remedy thins before...

I would be willing to have someone crawl into the ceiling to inspect the wiring there in that part (well, THIS part) of the house as often I find my CD player turned off, whereas it is left programmed to play a preset disc in a perscrinbed order, but something randomly cuts the outlet it's plugged into off, but fortunately not when my stereo and it are playing on...

The only GFI in the area is in the bathroom, as I gingerly pressed the reset for it, being that ferarful of your aforementioned shock or electrocution, as I view the tampering of it and the one in the kitchen to be unforgiving, no matter how much UL backs such equipment, I dislike the even minute need to have to touch those tiny buttons in between each outlet or do more than plug in and unplug electrical appliances/units/equipment....

Again, in the following evening, at 9:00 PM, to be exact, the electricity here/there came back on, I come home from work after midnight to find the porch light and a lamp I left on in my room to go on when our power came back, and everything else (even getting caught up in mostly to nearly all of my listening done) all on...

-- Dave

daveamkrayoguy-2019121212362706530_1.jpg

daveamkrayoguy-2019121212362706530_2.jpg

daveamkrayoguy-2019121212362706530_3.jpg
 
Dave,

So what happened after you pressed the GFI reset button? Did your lights come back on? If so, then the GFI being tripped was the reason for the outage. BTW, as long as your hands aren’t wet, touching the GFI reset button won’t give you a shock.

Now, if your lights just mysteriously came back on at 9 pm with no apparent reason, then sounds like you’ve got a loose wire connection somewhere, and this would worry me.

Eddie
 
Was your house built in a hurry?

If so, the electricians at the time may not have screwed the wires to the outlets and switches, they may have used the "stab" connections which will work themselves loose. That happened to my mothers house, they must have been in a hurry back in 1972 and used stab connections and over the decades, she has had parts of the house not have electricity. I am handy and know enough to solve the problem, that is, cut off the stab connections and make correct screw connections (turn the power off first and you might as well replace the outlet and switch too) or have an electrician you hire do this and might as well have him do the whole house.

To find out if the original builder was short of time, turn off power to a circuit or the whole house and unscrew out one of the outlets. If the wire is not around the side screw of the outlet and just is "stabbed" in to the back, you have a stab connection that is probably the issue.
 
Bob,

the possibility of “stab” connections is a very good suggestion for the reason Dave’s power is going out randomly in the bedroom. I would have never thought if this. Thankfully, when our home was built in 1980 I guess they weren’t in an all fired hurry and the connections for the outlets and switches were all made using the terminal screws.

Eddie
 
personal safety

DaveAMKrayoGuy, you know pretty much which outlets/lights are on the defective circuit. I would recommend you make sure they are off and/or unplugged. You want to get all loads off the circuit, so if there is a loose connection you will not have a load on it to induce an arc. Keep them off until you get a professional over to your house to diagnose and repair your problem.

You don't want an arc to occur and create a potentially lethal situation, such as a fire. Most deaths from electrically induced fires occur at night while the occupants are sleeping, so please use great caution.

As you have little background in residential wiring it is best (as in safer) that you do not attempt something you are uncomfortable with, and get a professional..

As you may not be aware of every item on that circuit, even better than just turning items off and unplugging would be to go down your row(s) of breakers systematically in your panel box and cycle (turn off then on) each one to see which controls the bad circuit and then keep that breaker off. However, you can only do this while you have current in the circuit and see which breaker turns off a light or other device on that circuit.

I know you said you don't want to switch breakers off and on because you "don't want to reset your clocks." However, you are going to have to make a value judgement on which is more important to you, resetting some clocks or preventing a potentially dangerous situation that could cause great harm.

Wishing you well.

-- Barry
 