The AVR (auto voltage regulator) will pick up in a reduction in voltage output and crank up the DC excitation voltage in the rotor to make up for this slack, adding more excitation volts will only increase real power to a point, but then reactive power production goes up if too much is added. The opposite can be said if there is an over voltage situation. Excitation voltage is also used to control the power factor. The power plant made 13.8kV off the end of all generators we had, and then we stepped it up to 138kV in the switching yard for transmission.
No, speed is not in proportion to the generators MW output. The speed is directly in relation to the frequency made. A two pole generator needs 3600rpm to make 60Hz power, 4 pole needs 1800rpm, 6 pole needs 1200.
Once the turbine was up to speed, 3600rpm (or 1800rpm for that junk Siemens machine) wed switch the boiler control to Boiler Follow (meaning the steam generator would slave to the turbine), then we used a synchroscope to bring it in phase with the grid. This can be done automatically, but best practice as taught to be by a bunch of old fellas was to sync it manually, nail the frequency, then put the syncroscope in auto, then close the breaker to the grid. The idea is if the auto sync system failed and switched to manual, its already set up in manual.
Once the breaker was closed on the turbine and it was on the grid, it was doing 3600rpm with no load, 0MW. On the 150MW turbine the boiler would be about 2% MCR (max continuous rating). We would then release the turbine control to the Electric Control Centre or ECC. At this point the plant was hands off. The turbine followed the grid demand, and the boiler/steam generator followed the turbines load demand. ECC would increase the MW demand at a steady and predictable rate taking care not to over stress or over load any of the equipment. Usually a MW a minute or so.
The entire time the turbine was spinning at 3600rpm, never changing speed. The torque demand is where the power is generated from and that was met by firing the boiler more. And since the boiler was in Boiler Follow mode and slaved to the turbine, if the turbine asked for more the boiler gave it. Adding excitation voltage increases the torque load of the flux lines the rotor has to cut through. Interesting enough the poles on a turbine generator are the rotor, and the stator windings are where the power is actually made. This is because the exciter windings are a lot less mass than the generator windings, and its something like the generator would be 4 times the size if that was the case. The logic for the turbine looked at its speed and the voltage output via the AVR for control and adjusted as necessary.
If you lost a turbine on a generator trip it was pretty scary. The whole place comes to a grinding halt in a split second. The breaker opens, that sends a trip signal to the turbine throttle, which sends a trip signal to the burners. It all cascades back and if youre lucky enough you wont pop a safety valve and wake the neighbors. The junk Siemens turbine had a dump valve on the inlet header so that any full load rejection shouldnt lift a safety valve. When a steam generator is making 1.5 million pounds of steam an hour and all of the sudden it doesnt have a place to put said steam...