Doug,
There is no real rocket science when it comes to converting from LP to Natural Gas and vice versa. You just need to know that you need to make it all safe.
Natural gas appliances usually run at 3.5" of water column and LP runs at 10" w.c.
So think in terms of a 3 to 1 ratio.
Natural Gas orifices are larger than LP orifices because of that pressure difference.
Assuming the dryer Does NOT have a standing pilot, you will need to install a larger opening orifice to get the equivalent btu's from the natural gas but if you cannot get a regulator kit to go back to natural gas, you MUST install an external regulator set for Natural gas for proper and safe operation. These are available from most major plumbing houses. You will probably have to put in reducing bushings to fit the piping on the dryer. This is to protect against variations in the supply pressure of the natural gas which can and does happen from time to time.
Ideally, you should tee off right after the regulator so you can connect a manometer to check and adjust the pressure while the burner is running. That way the burner will run at its designed parameter. The burners for LP and Natural are 99.9% the same so you should not have to change the burner.
There are orifice charts out there that will tell you the orifice size needed for a specific BTU rating at either natural or LP gas. If you know the burner rating on that dryer, post it here and I will be glad to look it up for you or provide a link to a useful chart.
Once you know the size of the orifice you will need, and theya re never going to go back to LP gas, then you can drill out the LP orifice to the proper size for Natural.
If you want, you can take out that orifice and go to Agway or AMerigas and give them the size you need and they can match an orifice to the one you have only with the enlarged opening.
Does this make sense?
I found a chart that you can use at the link attached.
Just go down the column under 3.5 and find your BTU rating. Then look over to the left and it will have a 2 digit number which is the orifice size and then a drill bit size if you wish to drill out the LP orifice. Hope this helps.
Steve