Uhm
Not sure
But green yellow will most likely NOT be a phase.
Green Yellow is the earth connection color over here.
Brown is phase, blue is neutral over here.
Given you want to get 240V out of 2 phases you will have to put both phases on the terminals, no neutral there, right?
So your phases on brown and blue, green yellow on the earth.
My best advice is to disconnect the machine IMMEDIATELY and to NOT PLUG IT BACK IT until you fixed that.
Maybe send a picture of the connections plus what kind of supply exactly you want to connect it to.
Not sure
But green yellow will most likely NOT be a phase.
Green Yellow is the earth connection color over here.
Brown is phase, blue is neutral over here.
Given you want to get 240V out of 2 phases you will have to put both phases on the terminals, no neutral there, right?
So your phases on brown and blue, green yellow on the earth.
My best advice is to disconnect the machine IMMEDIATELY and to NOT PLUG IT BACK IT until you fixed that.
Maybe send a picture of the connections plus what kind of supply exactly you want to connect it to.