continuing:
9905 - Motor Nominal Voltage
This is the voltage found on the nameplate of the motor.
230VAC
9906 - Motor Nominal Current
This is the current rating found on the nameplate of the motor.
1.6A
9907 Motor Nominal Frequency
This is the normal operating frequency of the motor. I could push the over what the motor is rated for, like what happines in the modern FL machines, but the is not necessary. It creates more problems in the long-run. I keep the value at the default, which is 60Hz.
9908 - Motor Nominal speed
This is the speed (RPM) rating found on the nameplate of the motor. There are 2 speed ratings on the nameplate, one for 50Hz, one for 60Hz. This motor will operate at a max of 60Hz, I use that rating. 3425 RPM.
Group 10: Command Inputs
1003 - Rotation direction lock
3 = Request
Group 11: Reference Select
1105 - EXT REF1 MAX The maximum frequency reference in HZ
I leave the default setting = 60Hz.
Group 12: Constant Speeds
1202 - Const speed 1 11.61Hz -tumble
1203 - Const speed 2 48.96Hz -Spin
1204 - Const speed 3 15Hz (DEFAULT)
My calculations for determining the speeds that I need are approximate.
Group 13: Analog inputs
1301:Minimum AI1
Minimum value of AI1 in percent. Defines relative anaog input value where frequency reference reaches minimum value
0%
Group 15: Analog ouputs
1503:Ao Content Max
Define output frequency where analog output reaches 20mA
I leave this at the default = 50Hz
Group 20: Limits
2003:Max Current
Maximum output current of the VFD
Range: 0.5 * I_n - 1.5 * I_n, where I_n is nominal current of the ACS 140
This is set to 4.5 A
2008:Maximum Frequency
This is the maximum output frequency of the VFD
The range is 0-300 Hz
Over driving the motor is not necessary
I set it to 60 Hz
Group 21: START/STOP
2102: Stop function
These are the conditions during motor stopping
I choose 1 = coast, rather than using dynamic braking
Group 22:Accel/Decel
2202:Accelerate Time 1
Ramp 1: time from zero to max frequency
10.0sec
2203
ecelerate Time 1
Ramp 1: time from max frequency to zero
5.0sec
2204:Accelerate Time 2
Ramp 1: time from zero to max frequency
60.0sec
2205
ecelerate Time 2
Ramp 1: time from max frequency to zero
60.0sec
Group 26:
2606: U/f below field weakening point
I keep this value at the default, as I want constant torque
1(LINEAR)
9905 - Motor Nominal Voltage
This is the voltage found on the nameplate of the motor.
230VAC
9906 - Motor Nominal Current
This is the current rating found on the nameplate of the motor.
1.6A
9907 Motor Nominal Frequency
This is the normal operating frequency of the motor. I could push the over what the motor is rated for, like what happines in the modern FL machines, but the is not necessary. It creates more problems in the long-run. I keep the value at the default, which is 60Hz.
9908 - Motor Nominal speed
This is the speed (RPM) rating found on the nameplate of the motor. There are 2 speed ratings on the nameplate, one for 50Hz, one for 60Hz. This motor will operate at a max of 60Hz, I use that rating. 3425 RPM.
Group 10: Command Inputs
1003 - Rotation direction lock
3 = Request
Group 11: Reference Select
1105 - EXT REF1 MAX The maximum frequency reference in HZ
I leave the default setting = 60Hz.
Group 12: Constant Speeds
1202 - Const speed 1 11.61Hz -tumble
1203 - Const speed 2 48.96Hz -Spin
1204 - Const speed 3 15Hz (DEFAULT)
My calculations for determining the speeds that I need are approximate.
Group 13: Analog inputs
1301:Minimum AI1
Minimum value of AI1 in percent. Defines relative anaog input value where frequency reference reaches minimum value
0%
Group 15: Analog ouputs
1503:Ao Content Max
Define output frequency where analog output reaches 20mA
I leave this at the default = 50Hz
Group 20: Limits
2003:Max Current
Maximum output current of the VFD
Range: 0.5 * I_n - 1.5 * I_n, where I_n is nominal current of the ACS 140
This is set to 4.5 A
2008:Maximum Frequency
This is the maximum output frequency of the VFD
The range is 0-300 Hz
Over driving the motor is not necessary
I set it to 60 Hz
Group 21: START/STOP
2102: Stop function
These are the conditions during motor stopping
I choose 1 = coast, rather than using dynamic braking
Group 22:Accel/Decel
2202:Accelerate Time 1
Ramp 1: time from zero to max frequency
10.0sec
2203

Ramp 1: time from max frequency to zero
5.0sec
2204:Accelerate Time 2
Ramp 1: time from zero to max frequency
60.0sec
2205

Ramp 1: time from max frequency to zero
60.0sec
Group 26:
2606: U/f below field weakening point
I keep this value at the default, as I want constant torque
1(LINEAR)