For starters let me thank Harry B (Kimball 455) for a super-nice time at the last Maryland wash-in. We travelled the town and really enjoyed each other’s company. Today we were discussing snail pans. I think of Harry a lot especially since his terrible loss due to a house fire.
I’d like to start by stating that I am an electronic engineer and CFEI (Certified fire and explosion investigator) who spent his career in the TV and appliance industry. I was the person who examined burnt TV and appliances and stopped such issues from recurring. For this reason I took much interest in Harry’s fire incident in his house - in a different way.
I am relaying my experience as an anecdote of GFCI (Ground Fault Circuit Interrupter) issues in my house.
I am aware of AC receptacle fires and after Harry’s experience I decided to just start a program of “renewal” of my GFCI receptacles. Our house is 15 years old and we have about 20 of these GFCI receptacles around. All seemed to work well through the years.
Although my receptacles worked well I thought it may be good to update my receptacles to new ones. Through the years I’ve replaced a few light switches and a few outlets but nothing chronic. I am critical. I like switches with a solid feel and outlets must always have a very strong grip.
Anyway, I start with the garage and replaced the GFCI outlets. I move on to the powder room, the laundry room and gradually update the outlets to new ones. I get about halfway through the house when life gets away from me and I stop. So far so OK. The original outlets are all clean, no discoloration but no branding. I suspect these are “builder’s grade” but I am not put-off by this as they have worked well for 15 years.
Some months later, the one outlet in the master bath is inoperative. It is rarely used but it has tripped. Nothing was plugged into that receptacle. I remember hearing a “snap” in the middle of the night but didn’t think much of it. I reset the outlet and all is well. I do a cursory mechanical and electrical check. Nothing seems amiss.
Several weeks later, the guest room GFCI has tripped. That outlet is never used. Check it again (again I am trained to detect receptacle failure modes) but see nothing wrong. I reset it and all is ok again.
Over the next upcoming weeks this occurs with different outlets and very randomly. This phenomenon is very new and quite odd. I am very aware of just about every aspect of the electrical system of this house and cannot immediately put my finger as to cause.
However, outside I see not one but two power-company trucks working on this block. Maybe there is a defect in the lines? Don’t know. I DID have a problem with the line transformer (line voltage fluctuations) a few years back and I did have a certified electrician do a thorough check of the circuit-breaker panel at about the same time. The breaker-box was “like new” per the electrician and the power company tighten the transformer connections. I didn’t think this was an issue but wasn’t sure.
And so I figured. I could go up to the power-company and advise them that I thought that the lines were tripping my GFCIs. However with no concrete proof as to cause they would likely accuse me of having old GFCI outlets.
I then finally noticed something.
ONLY the OLD GFCI outlets were tripping in what appears to be an erroneous manner. None of the new outlets is tripping unexpectedly.
Here I will now digress a bit. Bear with me.
I had to take my own advice. What do I mean by this?
Years ago I worked for a large TV manufacturer. We made one model of TV for hotels. It was a 19” color with AM/FM radio. Premium brand. Good unit and very reliable.
Anyway, hotel owner brought in a TV with a 2” high picture. (Vertical output failure). TV was about 7 years old. We replaced one capacitor and returned it.
Two weeks later he brings in three TVs. All have a 2” high picture. We replace the same capacitor in all three sets. He picks them up and goes home.
About a month later he brings in about five or six TVs. All have a small picture. He is totally fuming mad and yelling about our TV quality and that we have a big problem.
I explained to him my theory as to why they are all failing in the same way:
IF YOU HAVE:
The same product
From the same manufacturer
Of the same age
In the same environment
Used in the same way
Using the same components
With the same expected lifespan
Used in the same temperature
With the same line voltage
DO NOT expect the product to fail in a RANDOM fashion!
You will generally find the products to fail in the same way, at the same time.
He understood.
But to stop his fuming we offered a cheap flat-rate to fix the rest of the TVs. But that is beside the point.
And so my little speech came back to me. I had to take my advice. Are ALL my GFCIs failed at the same time for the reasons I speak of above?
To find out I replaced every remaining GFCI in the house over three days.
And every problem with the GFCIs evaporated immediately. I have never had a tripped GFCI since.
I suspect all of my GFCIs reached the same failure point at the same time.
I am thankful that Harry’s experience got me going on a GFCI replacement program. Had half of my GFCIs not been replaced I would have been perplexed. However with the important clue of half my GFCIs being new and not problematic, I was able to quickly remedy my situation.
WHEW! My fingers are tired of typing. All comments welcome.
[this post was last edited: 6/16/2019-13:08]
I’d like to start by stating that I am an electronic engineer and CFEI (Certified fire and explosion investigator) who spent his career in the TV and appliance industry. I was the person who examined burnt TV and appliances and stopped such issues from recurring. For this reason I took much interest in Harry’s fire incident in his house - in a different way.
I am relaying my experience as an anecdote of GFCI (Ground Fault Circuit Interrupter) issues in my house.
I am aware of AC receptacle fires and after Harry’s experience I decided to just start a program of “renewal” of my GFCI receptacles. Our house is 15 years old and we have about 20 of these GFCI receptacles around. All seemed to work well through the years.
Although my receptacles worked well I thought it may be good to update my receptacles to new ones. Through the years I’ve replaced a few light switches and a few outlets but nothing chronic. I am critical. I like switches with a solid feel and outlets must always have a very strong grip.
Anyway, I start with the garage and replaced the GFCI outlets. I move on to the powder room, the laundry room and gradually update the outlets to new ones. I get about halfway through the house when life gets away from me and I stop. So far so OK. The original outlets are all clean, no discoloration but no branding. I suspect these are “builder’s grade” but I am not put-off by this as they have worked well for 15 years.
Some months later, the one outlet in the master bath is inoperative. It is rarely used but it has tripped. Nothing was plugged into that receptacle. I remember hearing a “snap” in the middle of the night but didn’t think much of it. I reset the outlet and all is well. I do a cursory mechanical and electrical check. Nothing seems amiss.
Several weeks later, the guest room GFCI has tripped. That outlet is never used. Check it again (again I am trained to detect receptacle failure modes) but see nothing wrong. I reset it and all is ok again.
Over the next upcoming weeks this occurs with different outlets and very randomly. This phenomenon is very new and quite odd. I am very aware of just about every aspect of the electrical system of this house and cannot immediately put my finger as to cause.
However, outside I see not one but two power-company trucks working on this block. Maybe there is a defect in the lines? Don’t know. I DID have a problem with the line transformer (line voltage fluctuations) a few years back and I did have a certified electrician do a thorough check of the circuit-breaker panel at about the same time. The breaker-box was “like new” per the electrician and the power company tighten the transformer connections. I didn’t think this was an issue but wasn’t sure.
And so I figured. I could go up to the power-company and advise them that I thought that the lines were tripping my GFCIs. However with no concrete proof as to cause they would likely accuse me of having old GFCI outlets.
I then finally noticed something.
ONLY the OLD GFCI outlets were tripping in what appears to be an erroneous manner. None of the new outlets is tripping unexpectedly.
Here I will now digress a bit. Bear with me.
I had to take my own advice. What do I mean by this?
Years ago I worked for a large TV manufacturer. We made one model of TV for hotels. It was a 19” color with AM/FM radio. Premium brand. Good unit and very reliable.
Anyway, hotel owner brought in a TV with a 2” high picture. (Vertical output failure). TV was about 7 years old. We replaced one capacitor and returned it.
Two weeks later he brings in three TVs. All have a 2” high picture. We replace the same capacitor in all three sets. He picks them up and goes home.
About a month later he brings in about five or six TVs. All have a small picture. He is totally fuming mad and yelling about our TV quality and that we have a big problem.
I explained to him my theory as to why they are all failing in the same way:
IF YOU HAVE:
The same product
From the same manufacturer
Of the same age
In the same environment
Used in the same way
Using the same components
With the same expected lifespan
Used in the same temperature
With the same line voltage
DO NOT expect the product to fail in a RANDOM fashion!
You will generally find the products to fail in the same way, at the same time.
He understood.
But to stop his fuming we offered a cheap flat-rate to fix the rest of the TVs. But that is beside the point.
And so my little speech came back to me. I had to take my advice. Are ALL my GFCIs failed at the same time for the reasons I speak of above?
To find out I replaced every remaining GFCI in the house over three days.
And every problem with the GFCIs evaporated immediately. I have never had a tripped GFCI since.
I suspect all of my GFCIs reached the same failure point at the same time.
I am thankful that Harry’s experience got me going on a GFCI replacement program. Had half of my GFCIs not been replaced I would have been perplexed. However with the important clue of half my GFCIs being new and not problematic, I was able to quickly remedy my situation.
WHEW! My fingers are tired of typing. All comments welcome.