As some of you know, finding a deep freezer of any shape or size since March is pretty tough.
So of course, I have one that needs replaced or fixed!
This is a Woods CF22.
Last fall, I got a high temp warning buzzer in the middle of the night. No big deal, we just transferred the remaining contents into another freezer.
Opened up the lid and let it finish thawing, and cleaned/dried it up.
symptoms were; Compressor extremely hot. But not making any abnormal noises.. Just minimal refrigeration.
...........something to work on over the winter I figured..............
Well, Didn't happen, and as more and more chickens get butchered here, will be needing freezer space soon. (that's when I discovered new freezers are non obtainium)
So, I put a piercing valve on the suction side of the compressor and attached my gauge. It draws down to about 8-10 inches vacuum. So I burped a little 134a into the line, My guess is about 1/3 of a can.. until I have about 2-3 lbs pressure on the suction side.
Refrigeration appears to be back to normal. Compressor only gets 'warm', not hot.
After 1 week, Suction pressure seems to be 'holding'.. so I'm thinking it's a very tiny leak.. may take several months, or years to lose that 2-3 ounces again.
Then, I noticed the frost on the suction line. about 1.5 inch worth of frost. The compressor hasn't shut down!! It's about 20 below zero in the box! This is with the zero to seven knob set on '4' (should be around 0 degrees) Funny thing, I can turn the knob down to '1', before it clicks off... but after a couple minutes I can turn the knob clear up to '7' before it clicks on.
There shouldn't be such a wide sweep between on or off should there??
Does the 'fine adjustment' screw do anything with how wide a gap there is to the on-off sweep? or is it mainly to dial-in the thermostat to what the knob is set at?
If my leak is a yearly or longer I may just recharge when needed.
But if it's a monthly thing, is there any 'stop leak' products that wont plug the capillary? Rectorseal shows a half ounce product just for home appliances... which I'm assuming most appliances use the cap as the 'throttle' instead of an expansion valve.
Thoughts on this?
So of course, I have one that needs replaced or fixed!
This is a Woods CF22.
Last fall, I got a high temp warning buzzer in the middle of the night. No big deal, we just transferred the remaining contents into another freezer.
Opened up the lid and let it finish thawing, and cleaned/dried it up.
symptoms were; Compressor extremely hot. But not making any abnormal noises.. Just minimal refrigeration.
...........something to work on over the winter I figured..............
Well, Didn't happen, and as more and more chickens get butchered here, will be needing freezer space soon. (that's when I discovered new freezers are non obtainium)
So, I put a piercing valve on the suction side of the compressor and attached my gauge. It draws down to about 8-10 inches vacuum. So I burped a little 134a into the line, My guess is about 1/3 of a can.. until I have about 2-3 lbs pressure on the suction side.
Refrigeration appears to be back to normal. Compressor only gets 'warm', not hot.
After 1 week, Suction pressure seems to be 'holding'.. so I'm thinking it's a very tiny leak.. may take several months, or years to lose that 2-3 ounces again.
Then, I noticed the frost on the suction line. about 1.5 inch worth of frost. The compressor hasn't shut down!! It's about 20 below zero in the box! This is with the zero to seven knob set on '4' (should be around 0 degrees) Funny thing, I can turn the knob down to '1', before it clicks off... but after a couple minutes I can turn the knob clear up to '7' before it clicks on.
There shouldn't be such a wide sweep between on or off should there??
Does the 'fine adjustment' screw do anything with how wide a gap there is to the on-off sweep? or is it mainly to dial-in the thermostat to what the knob is set at?
If my leak is a yearly or longer I may just recharge when needed.
But if it's a monthly thing, is there any 'stop leak' products that wont plug the capillary? Rectorseal shows a half ounce product just for home appliances... which I'm assuming most appliances use the cap as the 'throttle' instead of an expansion valve.
Thoughts on this?