Local fusing in the UK isn't actually primarily there to be an extra safety device.
Final ring circuits used in the UK to feed outlets are rated at 32amps. The fuse in the plug of an appliance (rated 13amps max) or, if the appliance is hardwired, a fused connection unit, are only required because the appliance's cable would not be able to withstand a 32A fault.
It's normal practice in most European wiring regulations to have appliances connected either via a plug-and-socket, or via a local isolating switch.
Outside of the UK, appliances are usually sitting on 16 or 20amp circuits (15 amp in the US) and do not actually require local fusing. However, it is pretty important to be able to disconnect them without having to switch a breaker off! So an isolating switch is certainly a good idea!
That being said, it's not unusual in European kitchens (including the UK and Ireland) to have dishwashers, washing machines, dryers etc plugged into outlets that are hidden away at the back of near-by cupboards. While they're accessible, they would not be very easy to reach in a fire situation.
There are also plenty of kitchens where the dishwasher is plugged into an outlet on the wall directly behind it that is totally inaccessible. Either in compliance with old regulations, or a DIY, or not-very-well-done, kitchen installation.
So, in reality, many dishwashers over here would not be any easier to disconnect than a US hardwired machine. You would still have to throw a breaker in a lot of cases!!
Modern kitchen installations here require an isolating switch for dishwashers (And any other integrated appliances) located on the wall above them. Or, an accessible plug and socket.
When we installed our integrated dishwasher, the electrician used a 15A non-fused round-pin plug behind the machine plugged into an outlet that is connected to a fused, switched spur above the machine on the wall. His logic was that if the fuse went in the plug behind the machine, we would have to remove the entire appliance to get access to it. So, he avoided using a standard plug. The level of protection is exactly the same as the fuse is in the spur unit.
Cooking appliances (Ovens and hobs) have always had to have 32A or 45A double-poll isolating switches near by.
Here's a switched spur unit : (For appliances up to 13amp @ 230V)
Holds a standard UK/Ireland fuse (as found in all of our plugs)