I'd bet 3.5-4 ton would be more than enough for that house. I'd be looking at the ductwork, particularly the return air to make sure it's not undersized, that will always make an oversized system perform like it's undersized. I believe a 5 ton system should have at least 2 18" returns.
13 years ago when I did our upstairs system, it was practically unheard of for contractors to offer Manual J here. I went with the one that did, but he fudged the numbers so much in the software that we ended up with an oversized system anyway.
Second time around, 8 years ago, I solicited bids again for the downstairs system and everyone was offering Manual J. I ended up going with the contractor who wanted to downsize our furnace from 100k to 60k, we kept the same 2.5 ton condenser as that was already sized correctly. The furnace has no issues keeping up and it runs nice LONG cycles in 1st stage and 2nd stage doesn't kick in until it's below 10º outside.
13 years ago when I did our upstairs system, it was practically unheard of for contractors to offer Manual J here. I went with the one that did, but he fudged the numbers so much in the software that we ended up with an oversized system anyway.
Second time around, 8 years ago, I solicited bids again for the downstairs system and everyone was offering Manual J. I ended up going with the contractor who wanted to downsize our furnace from 100k to 60k, we kept the same 2.5 ton condenser as that was already sized correctly. The furnace has no issues keeping up and it runs nice LONG cycles in 1st stage and 2nd stage doesn't kick in until it's below 10º outside.